4.12.2011 ob 11:01
Ko ste ravno pri debati o defrostih in zalogovnikih. V navodilih za Mitsubishi piše tudi tole, da je mozno da se defrost dela tako da preklopi 3 potni ventil in uporablja toploto iz bojlerja:
V mojem primeru je bojler 300l. Tega nimam vklopljeno, ker ko sem gledal defrost med talnm gretjem, je pobral toploto kar iz talnega. Sicer z defrostom kar hitro opravi in ni razloga da se to spreminja. Bi bilo zanimivo, koliko stopinj bi se ohladila v bojlerju voda ce bi bili defrosti vsako uro s preklopljenim switchom. Ampak potem bi pa morali spet bojler pogosteje greti.
DHW pomeni sanitarna voda
"
6.6.1. When defrost signal is received
In DHW mode the 3-port valve remains ON.
In heating mode the valve can be OFF enabling the Heat pump unit to defrost while keeping the heat in the heating circuit or switched to ON so
system is defrosted using accumulated heat.
Selection is made using Dip SW3-1
Table:
SW 3-1 Operation
OFF Remains OFF (defrost while keeping Heating circuit).
ON Switch to ON (switch to DHW circuit to defrost. The system defrosts using
accumulated heat for defrosting)."
V mojem primeru je bojler 300l. Tega nimam vklopljeno, ker ko sem gledal defrost med talnm gretjem, je pobral toploto kar iz talnega. Sicer z defrostom kar hitro opravi in ni razloga da se to spreminja. Bi bilo zanimivo, koliko stopinj bi se ohladila v bojlerju voda ce bi bili defrosti vsako uro s preklopljenim switchom. Ampak potem bi pa morali spet bojler pogosteje greti.
DHW pomeni sanitarna voda
"
6.6.1. When defrost signal is received
In DHW mode the 3-port valve remains ON.
In heating mode the valve can be OFF enabling the Heat pump unit to defrost while keeping the heat in the heating circuit or switched to ON so
system is defrosted using accumulated heat.
Selection is made using Dip SW3-1
Table:
SW 3-1 Operation
OFF Remains OFF (defrost while keeping Heating circuit).
ON Switch to ON (switch to DHW circuit to defrost. The system defrosts using
accumulated heat for defrosting)."