Tukaj je izvleček iz ALCO navodil za tex. ventile. Iz tega mislim, da ni vseeno kakšna temperatura pred ventilom....
Example........
A valve has to be selected for the following conditions:
• Refrigerant R 134a
• System cooling capacity 6.0 kW
• Evaporating temperature -10°C
• Lowest condensing temperature +25°C
•
Liquid temperature +20°C
• Pressure drop in liquid line 1.5 bar
Calculation:
1. Theoretical pressure differential:
Condensing pressure is Pc = 5.65 bar at +25°C
Evaporating pressure is P0 = 1.01 bar at -10°C
Differential pressure is Pc - P0 = 5.65 - 1.01 = 4.64 bar
2. Effective pressure differential across valve:
4.64 - 1.5 = 3.14 bar
3. Correction factors:
Correction factor KΔp for the pressure differential 3.14 bar
from table on page 28 for R 134a
Δp = 3.14 KΔp = 1.4
Correction factor Kt for liquid and evaporating temperature
from table on page 28 for R 134a at +20°C / -10°C
Kt = 0.88
4. Calculation of nominal capacity Q0 x KΔp x Kt = Qn
6.0 x 1.4 x 0.88 = 6.86 kW.